<div style="color:black;font: 10pt arial;">Cory,
<div><br>
</div>

<div>With all due respect, if you're proposing that a driven ground rod is a *substitute* for the green wire (or conduit in very old buildings), this expert says you are DEAD WRONG!!  The safety provided by the green wire is not due to its earth connection.  Safety comes from providing a very low-impedance path back to the neutral at the main panel, so that fault currents (which range from 150 to 1,000A) will quickly trip the circuit's breaker. The essential connection for the green wire is to neutral, NOT to earth ground. In my seminars I have a slide that schematically shows this "clean ground rod" tied to outlet 3rd prongs *instead" of "that noisy green wire*.  If an equipment fault occurs, the chassis of the faulty equipment stays at or near 120 volts and the little current that flows between the new "clean" ground rod and the ground rod at the building power entrance (the only path now left to the fault current) is very small - not nearly enough to trip the circuit breaker - so the faulty equipment remains a lethal shock hazard!
<div><br>
</div>

<div><br>

<div>I sat in on a CEDIA seminar by an alleged expert (owner of a company that was hyping its power conditioning gear) who proposed exactly this idea.  He had the nerve to argue with me!  Fortunately for me, there was a master electrician in the audience, who cited Code and explained why doing so is potentially lethal. If someone gets a bad shock or is electrocuted, you will be hit with a lawsuit that will wipe out your company ... yes, it's happened. The judge won't give a rat's ass how the hum went away - fact is, your modification will be the cause of injury or death. The guy who presented this life-threatening information was banned from CEDIA when I reminded them of their legal liability.  This seems to be one of those "zombie ideas" that just won't die ... but this one is particularly dangerous!  All that being said, Code does allow for additional earth grounding, but the path provided by the green wire must never be interrupted (and must stay inside the same conduit as the line and neutral conductors of the circuit it protects - for reasons of inductance and path impedance under fault conditions.</div>

<div><br>
</div>

<div><br>
</div>

<div>Bill Whitlock</div>

<div><br>
</div>

<div>Whitlock Consulting</div>

<div><br>
</div>

<div>Ventura, CA</div>

<div><br>
</div>

<div>AES Life Fellow, <span style="font-size: 10pt;">IEEE Life Senior, and </span><span style="font-size: 10pt;">UL Pro Audio Advisory Panel member</span></div>

<div>
<div><br>
</div>

<div><br>
<br>
<br>

<div style="font-family:arial,helvetica;font-size:10pt;color:black">-----Original Message-----<br>
From: Corey Bailey Audio Engineering <proaudio@baileyzone.net><br>
To: proaudio <proaudio@bach.pgm.com><br>
Sent: Mon, Nov 4, 2019 4:10 pm<br>
Subject: Re: [ProAudio] AES on the west coast, was Re: Ampex/ProAudio List Dinner<br>
<br>

<div id="yiv5465265291">
<div>
    
<div><font face="Arial">Jim Brown, Bill Whitlock & David
        Josephson:</font></div>

    
<div><font face="Arial">All great advice,</font></div>

    
<div><font face="Arial">For equipment that I want to be truly ground
        isolated, I use a driven stake (Grounding Rod) and avoid AC
        ground if at all possible (local electrical codes be damned!).
        Then, follow the advice of someone who's knowledgeable on the
        subject of proper grounding. (Like, any of the three mentioned
        above.)</font></div>

    
<div><font face="Arial">Cheers!</font></div>

    
<div><font face="Arial">Corey</font><br clear="none">
    </div>

    <pre class="yiv5465265291moz-signature">Corey Bailey Audio Engineering
<a rel="noopener noreferrer" shape="rect" class="yiv5465265291moz-txt-link-abbreviated" target="_blank" removedlink__60e0b437-1a2e-4864-8f50-6e1c92f87382__href="http://www.baileyzone.net">www.baileyzone.net</a></pre>
    
<div class="yiv5465265291yqt5262827957" id="yiv5465265291yqtfd47978">
<div class="yiv5465265291moz-cite-prefix">On 11/4/2019 10:18 AM, Jim Brown wrote:<br clear="none">
    </div>

    <blockquote type="cite">On
      11/3/2019 7:38 PM, David Josephson wrote:
      <br clear="none">
      <blockquote type="cite">For instance as Jim Brown says, every
        conductor is an antenna.
        <br clear="none">
      </blockquote>
      <br clear="none">
      My favorite quote on this topic is from Henry Ott, who in his
      lectures spoke of the hidden schematic lurking behind the ground
      symbol. Since my retirement, I've been devoting my energies to ham
      radio, teaching fundamentals to folks with a wide variety of
      technical backgrounds. No surprise, the Pin One Problem is a hot
      topic -- Neil Muncy repeatedly told me that it was the primary
      mechanism behind RFI, and work for a paper that David and I
      co-authored in 2003 proved it. Fast forward to today, Pin One in
      CATV and DSL systems is the cause of EGRESS of RF noise that
      pollutes the radio spectrum.
      <br clear="none">
      <br clear="none">
      I do, however, strongly object to the phrase "ground loop,"
      instead using Bill's excellent model showing the mechanism as a
      difference in potential chassis-to-chassis between interconnected
      equipment (or chassis to ground) t as the cause of shield current,
      whether that difference is created by IR drops in green wires or
      antenna action. The reason I so strongly object is the that
      solution, especially in small very local systems, is so often
      proper bonding, which visually creates a loop with signal
      conductor shields. I'm thinking here of a home entertainment
      system or a ham station. I use a drawing of Bill's model in my
      talks and on-sine tutorials.
      <br clear="none">
      <br clear="none">
      I stopped teaching at trade shows several years ago because I was
      unwilling to participate in one held in Florida, in protest of the
      acquittal of that vigilante murder and the law that allowed it.
      <br clear="none">
      <br clear="none">
      As to our conventions -- my interest has always been in the papers
      and workshops, and hanging out with colleagues. In retirement, I
      can no longer justify the cost of a convention that requires a
      hotel stay in an expensive city.
      <br clear="none">
      <br clear="none">
      Henry Ott also did a great breakdown on the inductance of a wire
      as part of a loop.
      <br clear="none">
      <br clear="none">
      Jim Brown
      <br clear="none">
      <br clear="none">
      <br clear="none">
      _______________________________________________
      <br clear="none">
      ProAudio mailing list
      <br clear="none">
      <a rel="noopener noreferrer" shape="rect" class="yiv5465265291moz-txt-link-abbreviated" ymailto="mailto:ProAudio@bach.pgm.com" target="_blank" removedlink__60e0b437-1a2e-4864-8f50-6e1c92f87382__href="mailto:ProAudio@bach.pgm.com">ProAudio@bach.pgm.com</a>
      <br clear="none">
      <a rel="noopener noreferrer" shape="rect" class="yiv5465265291moz-txt-link-freetext" target="_blank" removedlink__60e0b437-1a2e-4864-8f50-6e1c92f87382__href="http://bach.pgm.com/mailman/listinfo/proaudio">http://bach.pgm.com/mailman/listinfo/proaudio</a>
      <br clear="none">
    </blockquote>
  </div>
</div>
</div>

<div class="yqt5262827957" id="yqtfd41589">_______________________________________________<br clear="none">ProAudio mailing list<br clear="none"><a shape="rect" ymailto="mailto:ProAudio@bach.pgm.com" rel="noopener noreferrer" removedlink__60e0b437-1a2e-4864-8f50-6e1c92f87382__href="mailto:ProAudio@bach.pgm.com">ProAudio@bach.pgm.com</a><br clear="none"><a shape="rect" target="_blank" rel="noopener noreferrer" removedlink__60e0b437-1a2e-4864-8f50-6e1c92f87382__href="http://bach.pgm.com/mailman/listinfo/proaudio">http://bach.pgm.com/mailman/listinfo/proaudio</a><br clear="none"></div>
</div>
</div>
</div>
</div>
</div>
</div>